Hi, WinCC flexiblecannot archive faster than 1 sec. That is system-related. If you want to archive for a short time you can use bittriggered trend with switch buffer. The data are stored in a data block. After the archive processthe stored datain DBcan be archivedin a csv filewith a WinCC flexible script. Maybe this FAQ will help you: http://support.automation.siemens.com/WW/view/en/21913875 Alternative you can use WinCC V6.2 SP2 or WinCC V7 because WinCC can archivetags every 500ms. If you need a faster archiving with WinCC (not WinCC flexible) you can use the following application: http://support.automation.siemens.com/WW/view/de/23780904 Bye |