Hi esantos I'm not surprised with what you observe and the reason is probably twofold:
|
|
Cheers |
|
| 8/27/2020 6:05 PM | |
|
Joined: 11/17/2010 Last visit: 12/28/2025 Posts: 108 Rating:
|
Hi Frink, I'm using one 414-2DP - 6ES7414-2XK05-0AB0 with Firmware 5.1. Thanks! |
|
Best regards, |
|
| 8/28/2020 12:53 AM | |
|
Joined: 10/7/2005 Last visit: 1/19/2026 Posts: 3054 Rating:
|
You could call the timer right away a second time so that it sees an RLO of 0 and is ready to started again in the next scan (or OB34 call). This won't help you with the S5 Timer inaccuracy itself though and the million $ question is: What is it that are you actually trying to achieve? Using the CPU 's clock bits or reading out the system time via SFC1 READ_CLK or using SFC64 TIME_TCK etc. are all based on the internal real time clock and will be far more accurate (although the CPU's real time clock drifts too as per CPU spec). IF a 100ms OB34 is already there, you could of course also simply add up an INT by 1 on every call and check when it reaches 10 to get a 1 second indicator. Back to the million $ question is: What is it that are you actually trying to achieve? (or why do you think you need an S5 Timer to achieve it) |
|