(1)| 4/6/2017 2:24 PM | |
|
Posts: 20 Rating:
|
Hello, The problem was a PLC logic and I have just fixed it. Thanks for your helping. |
This contribution was helpful to
|
|
| 1/30/2018 8:59 AM | |
|
Posts: 8092 Rating:
|
Hello chuot_bac, Please check if NC, PLC communication is established, the staus of 7 segment display on NCU box, please check PLC logic, infeed module pulse enable, drive enable commands are ON. Check the axes configuration. HTH. |
| 1/30/2018 9:11 AM | |
|
Posts: 20 Rating:
|
Hi, In my case DC screws on S120 modules were not enough tightened. After tightening the fault has disappeared immediately. |