(4)| 1/5/2021 10:34 AM | |
|
Posts: 7 Rating:
|
Sorry, my mistakeAttachmentOil Protection.zip (244 Downloads) |
| 1/5/2021 10:50 AM | |
|
Joined: 12/18/2014 Last visit: 12/29/2025 Posts: 36382 Rating:
|
I added two more threshold triggers. These have "0-20mA" as a sensor type. 0 mA corresponds to 0 units, 4 mA corresponds to 200 units. The output of the threshold trigger switches on at 0,0 mA and off at 3.8 mA. You only have to specify where you connect the outputs of the threshold triggers.
AttachmentLub Oil_V2.zip (237 Downloads) |
This contribution was helpful to
|
|
| 1/5/2021 11:14 AM | |
|
Posts: 7 Rating:
|
Amazing!! Thanks a Lot! |
This contribution was helpful to
|
|
| 1/5/2021 2:55 PM | |
|
Joined: 12/18/2014 Last visit: 12/29/2025 Posts: 36382 Rating:
|
|