(2)| 1/26/2021 2:31 AM | |
|
Joined: 9/9/2015 Last visit: 12/5/2025 Posts: 732 Rating:
|
My personal preference, i do not like to use CS. It is very complicated and sometimes , easier to lead to an error. We must be very sure on the logic behaviour on using CS. My take is , i will create a "parameter", name "X", and control the strategy using the "X", which i know the "X" is fully controlled by me and will not lead to an error. I would also create one more POSINO output to map POSINO. POSINO is position text to show notes on the screen, then, i will create POSINO_INT to do internal logic. Same concept, full controlled by myself. Hope it helps. |
|
Please give me 5 stars Rating if my post is helpful for you. :) |
|
This contribution was helpful to
|
|
| 1/26/2021 7:50 AM | |
|
Joined: 3/14/2008 Last visit: 1/15/2026 Posts: 2233 Rating:
|
Hi, Well Control Strategies just mean the different phases that are possible for an equipment. If you have an equipment with a warm and cold water valve, a PID controller and analog valve, the equipment can have phases. One phase could be Cooling and one could be Heating. The equipment is defined in the SFC and you can define two control strategies: Cooling (CS=1), Heating (CS=2). When the equipment is sent to Batch (SFC configured as EPH), you can use the equipment in the recipe procedure and you can define the same equipment phase to be run in Cooling or Heating. If you have created a setpoint, you can define if the setpoint is valid for one or both control strategies. If you have two setpoints like SPCooling and SPHeating, at the time you define the RPH (Recipe Phase), you can assign CS1 or CS2 and the correct setpoint appears. The use of control strategies in a equipment module is called: Recipe awareness. Now, with the new concept as of V9.0, it is possible to create EPHT and EMT. It is basically possible to remove the phases from the equipment and implement them in the EPHT. When the EPHT is instanced, you connect it to batch and just initiate the phase. You can now design the equipment as EMT without control strategies. From the EPHT level, you can assign setpoints and sent them to the EMT. Basically, the equipment is not tied to a unit anymore, only the phase is and it is possible you create several phases: One EPHT as Cooling, one EPHT as Heating and just control the EMT under it. That said, it really depends on the application if you want/need CS to be used. If the equipment can only Heat, you won't need control strategies. |
|
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
|
|
Follow us on