(2)| 1/27/2021 7:03 AM | |
|
Posts: 198 Rating:
|
Hello Mohamed, After modifications to the CFC charts (connection addition, deletion etc.) , it is expected to compile and download the charts before enabling test mode. If at all the compilation and download of the charts is not done and the user clicks on Test mode activate button, the user will see a pop up stating, "Program change since the last compilation. Please compile chart and download to CPU. Register CPU for debugging?" If the user clicks on 'Yes' here, the test mode will still be enabled but it won't work (get updated) for the changes done. I have attached a screenshot of my logic which is not compiled and downloaded before enabling the test mode. You will be able to see that the test mode depicts a wrong output for the updated block with new input connection. Hope this helps! AttachmentTest_Mode_Without_Compilation.zip (196 Downloads) |