Hello CatCesar , As I understand , actually you have a single User System ES/OS and you need to migrate to ES/Master and Standby OS , correct ? or ES and OS Master with OS Standby . What's the PCS 7 version ? Below the main steps with a minimum change / modification for version 8.x 9.x : You need to start first with OS Server / Stanby configuration - In PCS7 you add a new PC Station With a WinCC Appl. (Stby.) and a CP Card if exist connected to the existing Subnet Network. - Open the properties dialog of the Standby OS. Switch to the "Target OS and Standby OS Computer" tab and select the path of the target OS Computer - Execute the Station Configuration Editor - Configure and loading the AS-OS Communication in NetPro - In your exixting Wincc Project , you change it to Multiuser project - you generate the server data Now for Client , you need to create a Terrminal Bus network , -Cretae a new PC with Client application , and you select the target OS server - Execute the Station Configuration Editor - and the same for other or you can create a Ref..Client For more information , SIMATIC PCS 7 Minimal Configuration SIMATIC PCS 7 V8.2 You can fine the same documents for other PCS 7 Version Regards |
This contribution was helpful to
|
|
| 3/5/2021 4:44 PM | |
|
Posts: 24 Rating:
|
We have two separate identical OS with PCS7 v71. The next we will make upgrade 2OS v71 - v80 - v82 - v90 - Os Redundant - SRV Reduntant + 3 client
|