HELLO, i used v90 with s7 1200 via modbus. it gives A7496 SON enable missing. i dont have connection for Digital input. All actions will be do via modbus. what should i do? thanks ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 4/25/2016 1:52:34 PMNew subject after splitting |
|
4/25/2016 6:59 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating:
|
Please read SINAMICS V: Positioning (IPos) and Speed Control (S) with a V90 via ModbusSON missing indicates that you have configured motor with holding brake & drive control signal bit 0 needs to set high. Check r29400 bit 00 status if it is 00, it must be set to 1. Please check P1215, P1216, P1217, P1227, P1228. |