10/9/2012 9:55 AM | |
Posts: 118 Rating:
|
Hi, I have an error message 300200 drive bus hardware fault. I think the controller is an 840 but not 100%. Any ideas why this error has appeared?
|
10/11/2012 2:45 PM | |
Posts: 118 Rating:
|
There is no error message on screen now. But if I turn power off to the machine and then back on again anything after 30mins the fault comes back again! |
10/11/2012 3:19 PM | |
Joined: 8/11/2009 Last visit: 4/26/2023 Posts: 10 Rating:
|
You say you cleared the PLC using the S4 switch. Did you use the proper sequence? There is a way to extinguishe the red led on the PLC side without actually clearing the PLC memory. Do you have and did you follow this sequence? AttachmentNCU_Replacement_Reset_Guide-washed.pdf (594 Downloads) |
Last edited by: robertcichon at: 10/11/2012 3:36 PMLast edited by: robertcichon at: 10/11/2012 3:19 PM |
|
This contribution was helpful to
1 thankful Users |
10/11/2012 5:09 PM | |
Posts: 118 Rating:
|
Still no joy! Only other thing now surely is to start replacing axis cards and the ncu |
10/11/2012 5:56 PM | |
Joined: 8/11/2009 Last visit: 4/26/2023 Posts: 10 Rating:
|
Could be problems with the 5VDC supply sourcing at the NCU or the drives. Bon Chance!
|
10/13/2012 8:48 AM | |
Posts: 118 Rating:
|
So do you think replacing ncu card maybe the best option to begin with? |