2/27/2024 9:37 AM | |
Joined: 2/1/2024 Last visit: 9/11/2024 Posts: 15 Rating: (0) |
Hi team, I have a PXC7.E400S controller and a Siemens RDY2000BN Thermostat (MSTP Protocol). I am trying to discover the thermostat via Bacnet references from ABT. But could get any positive solution. Thermostat Confg. MSTP MAC: 50, BAUD RATE: 19200, DEVICE ID: 10, MAX MASTER: 127, MAX FRAME: 10 Pls suggest possible solutions ------------------------------------------------------------------------------------------ Attachmentmstp.pdf (422 Downloads) |
Last edited by: Jen_Moderator at: 03/18/2024 12:01:48New subject after splitting |
|
2/28/2024 4:49 PM | |
Joined: 11/8/2017 Last visit: 10/8/2024 Posts: 337 Rating: (190)
|
Hi, The BACnet References section in the Engineering tab does not allow you to discover devices and their associated points in V5.1. This section is where you add and configure your BACnet points, after you know the required details. Have you tried a BACnet browser whilst connected to the controller? Can you please post a screen shot of the MSTP trunk configuration? Refer to the attached file Capture1.png. If any changes are made to the MSTP settings for the controller, these need to be downloaded into the controller. One way of doing this is shown in the attached file Capture2.png. Regards, AttachmentCaptures.zip (388 Downloads) |
Last edited by: CJ. at: 02/28/2024 16:59:08 |
|
This contribution was helpful to1 thankful Users |