In the manual (page 7), the wirin detail indicates channel 1 at terminals 1 and 2 (at left) and channel 2 at terminals 5 and 6 (right) is it. .? May be different module type came in my mind. . Sorry to misguide you. . If wiring is ok and mA also came as per actual. . Then try one thing. . Re defined process Image Input Area (e.g. 512) then assign address less than your PII area and then check your counts. . YESSS. That is the solution. you solved my problem for the second time this month. ThanksPranav J. Bhagat
|