Joined: 7/18/2016 Last visit: 9/6/2021 Posts: 6 Rating: (0) |
Thank you Denilson, as always a very informative post. My query is regarding whether or not the HSC can be simulated with PLCSim. I've upgraded the project to v15.1 and swapped the CPU to one with firmware version > 4.0 and selected the simulation support during block compilation under project properties --> protection. I then compiled all and downloaded hw & sw and I then toggle the clock generator input i0.0 but I do not see any change in the count value. Would I perhaps need PLCSim Advanced for this? ------------------------------------------------------------------------------------------ AttachmentHSC_V14_V15.1.zip (326 Downloads) |
Last edited by: Jen_Moderator at: 07/16/2019 09:32:25New subject after splitting |
|
7/17/2019 1:32 AM | |
Joined: 7/7/2010 Last visit: 11/15/2024 Posts: 15402 Rating: (2443)
|
Since you cannot check hardware with PLCSim, what software / logic are you wanting to check that toggling the count input would do? You can adjust your logic to move the count to an internal DB tag and use that internal DB tag for all the work with the count input. In this way, you can _intercept_ that count input MOVE or copy during simulation and use the PLC clock input and an edge detector to cause the count to change.
|
science guy |
|
This contribution was helpful to1 thankful Users |