5/27/2014 9:06 PM | |
Posts: 9 Rating:
|
I've sent the problem to the online support i hope they could make an update |
This contribution was helpful to
2 thankful Users |
5/27/2014 9:48 PM |
|
Joined: 10/19/2012 Last visit: 4/17/2022 Posts: 315 Rating:
|
I agree that they take corrective action my point is that they should not make mistake in first place
|
5/28/2014 5:15 AM | ||||
Joined: 5/28/2008 Last visit: 7/30/2024 Posts: 4514 Rating:
|
Hello AsAPLC Width of Active Bus Module for Power Supply = 97mm Width of 6 Nos. Active Bus Modules for SMs = 6x80 = 480mm Total Width = 577mm These will not fit on 530mm DIN Rain ( 6es7195-1gf30-0xa0 ) You need 620mm DIN Rail : 6ES7195-1GG30-0XA0 - ET200M, RAIL 620MM May be a Bug in the System Configurator Hope this helps Cheers Navnag Hello, As Navnag told Width of any bus unit is 97 mm. But when you install bus units on the racks, part of it is being inserted into the next bus unit. Please look at attached picture. Siemens provides Racks suitable for insert / remove function in many widthes.
Hope this helps. |
|||
Ayman Elotaify |
||||
This contribution was helpful to
1 thankful Users |
5/28/2014 7:49 AM | ||||
Joined: 1/17/2010 Last visit: 7/15/2024 Posts: 77 Rating:
|
dear ayman, you have mentioned that both racks 483 and 530 are suitable for 5 bus modules, but what i know that 483 rack is ok for 4 bus modules and 530 rack can fit 5 bus modules. please clarify. good luck
|
|||
5/28/2014 8:12 AM | |
Joined: 5/28/2008 Last visit: 7/30/2024 Posts: 4514 Rating:
|
Hellomostref You need 417 mm to install 5 bus modules. So if you installed them on the 483mm rack, the free space would be (483-417) = 66 mm. Please revise my explanation bellow which I published in previous post.
|
Last edited by: Ayman Elotaify at: 5/28/2014 8:17 AMLast edited by: Ayman Elotaify at: 5/28/2014 8:14 AMLast edited by: Ayman Elotaify at: 5/28/2014 8:14 AMLast edited by: Ayman Elotaify at: 5/28/2014 8:13 AMAyman Elotaify |
|