7/28/2023 11:59 AM | |
Joined: 4/14/2023 Last visit: 12/18/2023 Posts: 9 Rating:
|
Hello, I need to replace an ET200L with a ST200SP in a 1999 machine, I have the PLC backup, I changed the remote I/O for the IM 155 6DP HF in Simatic Step 7 V5.7, the software does not report any errors in the configuration , when I download the software for the S7400 the PLC goes into RUN but returns a profibus error, the IM 155 was recognized by the profibus network and everything seems to be ok, however I receive a profibus network error from two other network components which are two KEBA HT-401 hand controls and the system remains in error. In the hardware config these two controls appear with the GSD installed but I can only change the DP address and nothing else. When I download the original program back to the PLC with the ET200L everything works perfectly. So I think I must be doing something wrong when sending the download with the IM 155 in the software or something is getting lost in the process, I couldn't understand why this is happening, can anyone help me? Attachment2023-07-27 11_05_43-HW Config - [SIMATIC 400(1) (Diagnostics) -- Bkp_CartaoCPU_26_07_23 ONLINE].png (507 Downloads) |
Last edited by: AutoGen_8101027 at: 07/28/2023 12:02:57Last edited by: Jen_Moderator at: 07/31/2023 07:03:21Text formatting optimized. |
|
7/28/2023 1:12 PM | |
Joined: 4/14/2023 Last visit: 12/18/2023 Posts: 9 Rating:
|
The 3 modules show the same messages, however it only includes the IM 155, I didn't change anything in the other two.
Attachment2023-07-28 10_08_52-HW Config - [SIMATIC 400(1) (Diagnostics) -- Teste_27_07_23 ONLINE].png (529 Downloads) |
7/28/2023 1:48 PM | |
Joined: 4/14/2023 Last visit: 12/18/2023 Posts: 9 Rating:
|
I changed the control configuration parameter to disabled and the IM 155 was recognized and without faults, but address 120 and 122 are still faulty, could the IM 155 be causing some impediment for the other two to work correctly? since I didn't change parameters of 120 and 122... when I remove IM 155 from the program and download it to CPU400 everything works correctly again.
Attachment2023-07-28 10_42_26-HW Config - [SIMATIC 400(1) (Configuration) -- Teste_27_07_23].png (639 Downloads) |
7/28/2023 2:21 PM | |
Joined: 4/14/2023 Last visit: 12/18/2023 Posts: 9 Rating:
|
Yes, I noticed all these things, now I put the program with the ET200L at address 98, see that address 120 and 122 still have question marks as per your observation, but they are operational and recognized normally, and that's what I don't understand because I don't I made no changes to 120 and 122, only the change of address 98 to an IM 155, according to information from the Siemens manuals this change is perfectly possible, I need to make this replacement because the ET200L is malfunctioning and Siemens has discontinued this module. See attached image...
Attachment2023-07-28 11_09_49-HW Config - [SIMATIC 400(1) (Diagnostics) -- Eng_Benninger_17_04_23 ONLINE].png (433 Downloads) |
9/12/2023 1:29 PM | |
Joined: 4/14/2023 Last visit: 12/18/2023 Posts: 9 Rating:
|
Hi Daniel, Today I managed a few more hours with our machine to collect the CPU 414 diagnostic buffer, below is the text file that was generated: [snip]
AttachmentFiles.zip (471 Downloads) |
Last edited by: Jen_Moderator at: 09/13/2023 07:51:51Diagnostic buffer and Screenshot added as .zip file. |
|
Follow us on