1/6/2018 12:01 PM | |
Posts: 20 Rating: (0) |
Hello, can I ask help in AM2 RTD module sample configuration for a temperature control? The logo guide is not clear at all between the differences in programming using this module or the standard AI input - I found some sample as Main principle of a two-point heating control (without hysteresis) but is not clear if there is used a standard AI input or the AM2 RTD module input. I cannot find in any place the differences in programming with or without this module. It is an expensive module. Simplify the life or not? How? It is not still clear to me how to use the sensor type in the logo soft analog block also (when use the sensor PT100/PT1000?). Only when the sensor is "directly" connected to AI in the first block or also when it is connected to the AM2 RTD module and in the next not directly connected blocks? Thank you very much ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 1/7/2018 11:05:58 AMNew subject after splitting |
|
1/6/2018 3:18 PM | |
Joined: 12/18/2014 Last visit: 5/17/2024 Posts: 33052 Rating: (4082)
|
Here's an example of a heating mixer valve. The setpoint is automatically adjusted to the outside temperature. AttachmentMixing valve.zip (573 Downloads) |