4/11/2012 6:44 PM | |
Joined: 1/28/2009 Last visit: 6/11/2024 Posts: 6841 Rating:
|
Hello , And this is the project.SCL Source code is also provided.If you are not familiar to SCL,Only copy the "FB300" in your project and call it in OB3X. Note, time between 2 successive calls of OB3X is included in calculation so this time should be constant and provided for the algorithm in "Interval" input. Please, feel free to ask any question about the function.There are plenty of qualified members to help. Best regards, Hamid Hosseini AttachmentHD.zip (320 Downloads) |
This contribution was helpful to
1 thankful Users |
7/13/2012 5:53 AM | |
Posts: 36 Rating:
|
after processed in PID block, how to make a transfer function 2/(4s+1) of plant in S7? thanks Firza |
7/13/2012 10:12 AM | |
Joined: 1/28/2009 Last visit: 6/11/2024 Posts: 6841 Rating:
|
Hello , Finally data related to solving ODEs published publicly here: Numeric Methods to Solve ODEs(Ordinary Differential Equations )For your case refer to "1-First Order Differential Equation"which FB1 written in SCL provide numeric solution to equation you have presented. Best regards Hamid Hosseini |
Last edited by: hdhosseini at: 11/26/2014 11:35 AMLast edited by: hdhosseini at: 8/16/2015 4:57:12 PM |
|
7/13/2012 1:12 PM | |
Posts: 378 Rating:
|
Well done hdhosseini Thank you so much !!! . |
Last edited by: desmul24 at: 7/13/2012 1:17 PM |
|
This contribution was helpful to
1 thankful Users |
11/18/2014 12:49 PM | |
Posts: 1 Rating:
|
Dear Marko; Can you also provide this simpler method for the first order?
|