3/6/2014 11:25 AM | |
Joined: 9/22/2010 Last visit: 2/10/2025 Posts: 225 Rating:
|
Hello Valerio, in general as soon as athe Modbus block recognizes a valid license, the SF should no longer flash. If it still flashes eventhough you have a valid REG_KEY, I would recommend to check the following FAQ: Why is the status value A090 (hex) output for Modbus TCP although you have entered the correct license? Regards, Sakura |
This contribution was helpful to
1 thankful Users |
3/6/2014 12:15 PM | |
Posts: 23 Rating:
|
Hello Sakura and many thanks. I see the adviced FAQ regarding error code A090 (hex) and analized every remedy. Attached You can find my Modbus DBs. In my opinion it is strange that: in DB-param at line 38.0 LICENSED=TRUE while in the CONTROL-DAT DB at line 33.0 LICENSED=FALSE By means of a modbus tcp/ip simulator it was possible to check all my input register from CPU315-2PN/DP, so my conclusion is "it works". Note: the modbus communication is by CPU-PN Maybe there is some problem with OB121 PROG_ERR (Remove call of the Modbus block from OB121, see a/m FAQ), but my OB121 is empty. Otherwise I can broke SF led Regards. Valerio AttachmentREG_KEY-IDENT_CODE.pdf (1566 Downloads) |
3/6/2014 4:04 PM | |
Posts: 23 Rating:
|
Well, attached step by step my Modbus TCP wizard in order to check my Modbus DBs. First of all, please note that I choose to exclude Modbus TCP from redundancy, each CPUs has own Modbus that works separately, with 2 nos. license, so I prefer that:
So far it seem that CPU works correctly: SW redundancy ok, Modbus TCP ok, only flashing SF led for missing license (A090). Many thanks Sakura AttachmentModbus TCP wizard.pdf (1190 Downloads) |
Last edited by: valerio.albo at: 3/6/2014 4:06 PM |
|
3/28/2014 10:21 AM | |
Posts: 23 Rating:
|
Hello Sakura, I'm testing my PLC and slow flashing LED is still present. Program works correctly, both sw redundancy and MODBUS TCP/IP, but I'm trying to remove the problem regarding MODBUS license without any result. I'm attaching all DBs that contain information regarding Modbus license. If necessary I will send you whole program, please indicate me how to do. Thanks in advance. Valerio Albo AttachmentModbus license.pdf (744 Downloads) |
3/28/2014 3:58 PM | |
Posts: 23 Rating:
|
Hello Kaulquappe, many thanks ... Now we try but MOD_PARAM is configured by Modbus TCP wizard (see attached), maybe shifting end address for data area (i.e. from 14 to 20, I don't know exactly). I'm not sure what to do, please be so kind to help me. Attachmenterror code and wizard.pdf (577 Downloads) |
3/28/2014 5:20 PM | |
Posts: 23 Rating:
|
Hello Kaulquappe I'm posting my OB100, maybe the problem is here, or not. However I only change the number of DB of the example. I have to delete the online DB? Or exist a procedure to follow? Many time I have tried with STOP/RUN of the CPU by means of its selector on the frame. Or I do this operation by PC forcing STOP/RUN via buffer diagnostic? A big prize for the solution! Anyway I seem that the end is near ... the light at the end of the tunnel AttachmentOB100.pdf (670 Downloads) |
3/31/2014 9:00 AM | |
Posts: 23 Rating:
|
Hello Kaulquappe, attached my OB1. Take note that, in this program there are Modbus TCP and software redundancy, as you saw in my OB100. This morning I try again ... anyone have any suggestions is welcome AttachmentOB1.pdf (626 Downloads) |
4/3/2014 5:39 PM | |
Posts: 23 Rating:
|
or in the IDB_MODBUS, first row ID? or both IDB_MODBUS and OB100? others? |
4/4/2014 3:09 PM | |
Posts: 23 Rating:
|
Hello Sakura I have a connection for each CPU, anyway I've already tested your instruction but the problem is always the same, working modbus with no license, or license with no working modbus. So I think, are there some mistakes in my IDB_MODBUS? In my attached DB shall I to change address 0.0, 2.0, 348.0 and 350.0? AttachmentIDB_MODBUS.pdf (624 Downloads) |
4/4/2014 4:14 PM | |
Posts: 23 Rating:
|
Thanks in advance, please take note that ID=9 attachment:
AttachmentOB1-OB100-DBs.pdf (578 Downloads) |
4/4/2014 5:02 PM | |
Posts: 23 Rating:
|
Hello I have different ID, ID=8 for the first CPU, ID=9 for the second CPU. In the previous post I attached OBx and DBs for the second CPU. Now I am attaching also CONTROL_DAT DB. Modbus TCP is not in the software redundancy. Hence two CPUs, with two modbus, with two different ID, in order to avoid any problem with the redundancy. AttachmentDB100.pdf (521 Downloads) |
4/7/2014 10:54 AM | |
Posts: 23 Rating:
|
Hello I'm checking the Modbus example to try to find any errors, and I have found that FB104 is used both sw redundancy and MODBUS TCP, so I decided to use FB104 SWR_AG_COM (for sw redundancy) because my modbus is server (not client). Is it a problem? And if yes, what can I do? AttachmentFB104.pdf (580 Downloads) |
4/7/2014 12:01 PM | |
Posts: 23 Rating:
|
Hello Sakura, don't worry, I call the support. How is it possible to rewire the FB104? I'm afraid to rewire, what happen in FB104 SWR_AG_COM? I see a FAQ that explain what I do but I'm not sure how to do, can you help me? Step by step if possible, see attachment Attachmentrewire.pdf (611 Downloads) |
4/7/2014 4:59 PM | |
Posts: 23 Rating:
|
Hello, I supposed the same problem and I tried with end address 30 but I have the same error, is it wrong? |
Last edited by: valerio.albo at: 4/7/2014 5:17 PM |
|
4/7/2014 5:21 PM | |
Joined: 9/22/2010 Last visit: 2/10/2025 Posts: 225 Rating:
|
How large is your DB90? |
This contribution was helpful to
1 thankful Users |
4/7/2014 5:28 PM | |
Posts: 23 Rating:
|
hello attached my DB90 AttachmentDB90.pdf (754 Downloads) |
4/8/2014 11:19 AM | |
Posts: 23 Rating:
|
Hello, I've done it! I fixed my DB90 following the example and now it all works |
This contribution was helpful to
1 thankful Users |