1/19/2012 12:54 PM | |
Joined: 6/29/2010 Last visit: 10/27/2022 Posts: 112 Rating: (63) |
Hello guys, Here is a sample program of S7 communication betweenthree S7 1200 CPUs (thePLC1 reading data from PLC3 and writing data in PLC2). AttachmentS7 1200 GET_PUT.zip (8215 Downloads) |
Last edited by: MrPaiva at: 1/20/2012 4:23 PMLast edited by: MrPaiva at: 1/19/2012 8:13 PM |
|
This contribution was helpful to15 thankful Users |
6/26/2012 11:26 PM | |
Posts: 1 Rating: (0) |
Damaged file no longer functional it seems that if SEIMANS wanted to sell more of the S7 1200 unitsthey would have more sample files available |
10/9/2012 11:44 AM | |
Joined: 9/23/2005 Last visit: 5/21/2024 Posts: 4326 Rating: (1426)
|
Hi, Updatesfor STEP7 / WinCC SP2 (use the update 4l): |
Denilson Pegaia |
|
10/17/2013 9:53 PM | |
Joined: 7/7/2010 Last visit: 5/17/2024 Posts: 14751 Rating: (2372)
|
SebOberI am a little surprised you were able to get your GET/PUT to work if you followed your own advice exactly as written. In my experience, the P#DB#.DBX0.0 BYTE 2 or P#DB#.DBX0.0 WORD 1 are supposed to mean the same and mean a single 16-bit chunk of data is being passed. If P#DB#.DBX2.0 BYTE 4 is used, it means start at word 1 (2 bytes offset from beginning of DB) and pass the next 4 bytes or 32-bits or 2 16-bit words worth of data. By reading your explanation, you seem to have BYTE where WORD should be in at least a couple of places. Thanks for the helpful tips, just be careful of the terminology. It may be that TIA Portal works even if we tell it the wrong values for GET/PUT, but perhaps some day they will change it and close any loopholes that let us read further into a DB that we say we passed via a pointer. |
science guy |
|
Follow us on