4/30/2016 10:54 AM | |
Posts: 8946 Rating: (999) |
Online? SFC12 may be the solution. |
This contribution was helpful to1 thankful Users |
4/30/2016 10:57 AM | |
Joined: 5/28/2008 Last visit: 11/6/2024 Posts: 4516 Rating: (839) |
It's possible but you have to insert the suitable error OB in order to avoid entering the Stop mode. AttachmentUsing error OBs in your program (1).pdf (795 Downloads) |
Ayman Elotaify |
|
This contribution was helpful to1 thankful Users |
4/30/2016 11:57 AM | |
Joined: 2/15/2010 Last visit: 1/20/2024 Posts: 329 Rating: (6) |
Dear, How about hardware connection modifications? |
Hazem |
|
4/30/2016 12:01 PM | |
Posts: 8946 Rating: (999) |
Removing the plug? Or what do you mean? |
4/30/2016 12:12 PM | |
Joined: 5/28/2008 Last visit: 11/6/2024 Posts: 4516 Rating: (839) |
That's another issue. If you want to make this, then you should think about CiR "Configuration in Run" Here's some of many links to learn more about CiR.
Hope this helps. |
Ayman Elotaify |
|
Follow us on