2/25/2025 8:30 AM | |
Joined: 2/17/2020 Last visit: 8/29/2025 Posts: 1251 Rating:
|
Hi again, You don't have the original WinCC Flexible project downloaded in OP73? This could be an issue since OP73 devices do not support "back transfer" functionality to get the project downloaded and be able to edit it. Please see: How do you back transfer the projects of an operator panel and what should you watch out for? |
A rating will be well appreciated. |
|
2/26/2025 8:55 AM | |
Joined: 2/10/2025 Last visit: 5/19/2025 Posts: 24 Rating:
|
Fortunately we had the original project, it was integrated with the plc project, which i thought would be an issue, however i was able to open the project in wincc flexible 2008 sp3, i was already connected to the plc which was connected through profibus to the op73, so i connected into the profibus , started runtime in the op73 project and it connected to my plc and i was able to use the PG laptop as the HMI, my PG was setup to us CP5611 (Auto) mode. |