Is there a parameter in the S120 drive that turns on when the drive has reached the set speed? |
9/1/2010 9:35 PM | |
Joined: 6/4/2008 Last visit: 8/5/2025 Posts: 1518 Rating:
|
Hi, unfortunately, nothing quite so simple in Sinamics. Take a look at Function diagram 8011 in the S120 List Manual You then have to set up hysteresis (P2164) and threshold value (P2163), finally, you can use the status bit r2197.7 as n_set=n_act. Cheers, Graeme |