Posts: 22 Rating:
|
How to setup one HMI TP170B for two S7-300. This would be a new application for me. Greatlly appreciated Randy |
5/10/2011 2:38 PM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Make 2 connections off the S7300 type, use different PLC adresses, You can now choose when making the tags, witch connection to use. Have attached picture to explain a bit more Best regards, Marcjan Attachment2plc.pdf (153 Downloads) |
Problem solved? |
|
5/10/2011 2:43 PM | |
Posts: 22 Rating:
|
A picture worth a thousand words... Thanks I'll try it. |