6/10/2011 10:49 PM | |
Posts: 13 Rating:
|
Hi! I need to print report for every month and also get values to wincc alarm log display.I have tryed to print report. Printing works fine, but some how the tag values is always displayed with default values?? I want also save tag datas to exel CSV after machine sequense overs and get time stamp to it. Do I need to made it with history logs or? I have S7-1200 and WinCC flex RT for that. Is there any sample program for my need? I would be very thankful about to get help. I have only couple day for do that job and I don't wanna dissarpoint client.. Sorry my language.. Splitted from saving reports that i make for my recipe. |
Last edited by: O_Moderator at: 6/14/2011 9:03 AMnew subject after splitting |
|
6/14/2011 9:27 AM | |
Joined: 4/29/2010 Last visit: 1/20/2025 Posts: 1557 Rating:
|
Hello,
check the aquisation trigger of the tags wich are displayed in your report. They must be set to cycle continues if you want to show the actual values of this tag in a report.
Yes you need to add a historical log. At this faq you can find a guideline: How are tags and alarms logged in WinCC flexible? best regards |