Hello danny kezada I'd agree with viralpatel's advise in this case and go fora direct connection of one HMI to your fiveS120 drives via Profibus. Apart from saving you some money on the PLC, the main advantage of the HMI readingdirectly from the drives is that you can easily access a wide range of parameters (The PLC is very good at doing fast cyclic data exchange, butyou'll need to resort to programmig of acyclic Parameter reads if you want more than the usual). Anyhow, below are a few hopefully helpful links and as far as only displaying Alarm messages & faults are concerned, the work is pretty much already done for you by Siemens: How do you establish a direct connection between HMI Panels and frequency converters (SINAMICS and Micromaster)? How do you set up a direct connection between panel and frequency converter in SIMATIC WinCC (TIA Portal)? How do you insert error messages of a frequency converter (SINAMICS and MICROMASTER) in a WinCC flexible or WinCC (TIA Portal) project? I hope this helps |