(10)| 5/13/2014 8:46 AM | |
Posts: 149 Rating:
hello, i want to know what is thedifference between Ics,Icu & Icw?
| 5/21/2014 7:44 PM | |
Joined: 5/28/2008 Last visit: 1/22/2026 Posts: 4522 Rating:
Hello, Yes. after twotimes of Icu, the circuit breaker should be changed or tested again to ensure it can withsyand with the short circuit current or not. As I told before:
Please see thislink Hope this helps.
Ayman Elotaify |
| 4/26/2019 2:41 PM | |
Posts: 1 Rating:
What I want to know, is what is the difference between Icn and Icu. |
| 2/28/2020 8:43 AM | |
Posts: 1 Rating:
The rated breaking capacity (Icu) or (Icn) is the maximum fault-current a circuit-breaker can successfully interrupt without being damaged. The probability of such a current occurring is extremely low, and in normal circumstances the fault-currents are considerably less than the rated breaking capacity (Icu) of the CB. for more details you can visit following https://www.theelectricalcontractors.org/what-is-ics-icu-of-a-circuit-breaker/ |