4/23/2007 11:28 PM | |
Posts: 177 Rating:
|
Thanks, would this still apply even though I am unable to see the tags in tag explorer when I try to import through alarm logging? Regards, henno2000 |
4/24/2007 8:44 AM | |
Posts: 1084 Rating:
|
Hi, Did you place a check in the checkbox when trying to import (browse) ? See the attached picture for what I mean... with regards, Ikkezelf |
4/24/2007 11:33 AM | |
Posts: 177 Rating:
|
Yes, the box is checkmarked, but still no tags are displayed. |
4/25/2007 9:07 AM | |
Posts: 177 Rating:
|
Thanks, images attached AttachmentImages.zip (298 Downloads) |
4/25/2007 1:56 PM | |
Posts: 1275 Rating:
|
I've just come up with a quick "how-to" for creation of the analog alarms and their monitoring values... Check the attached file. I believe you'll have to create the analog alarms and their monitoring first. Then import the messages, since the limit monitoring will access existing messages only. In the messages' "Message Tag" field you still cannot use the floating points. AttachmentAnalog Alarm.pdf (335 Downloads) |
4/25/2007 2:03 PM | |
Posts: 1084 Rating:
|
Analog alarms is what I use also. They work great. Still I use them only with unsigned tags, but the idea is good Danielle. with regards, Ikkezelf |
4/26/2007 3:32 PM | |
Posts: 1084 Rating:
|
Yes, In the WinCC Information System which gets installed during the wincc install. |
4/26/2007 5:12 PM | |
Posts: 1084 Rating:
|
You can always use the wincc tag simulator to trick the tag... You can find it under start-> simatic -> wincc -> tools |
4/26/2007 5:36 PM | |
Posts: 177 Rating:
|
Would this work for tags that are imported through OPC (as in this case?) I have tried applying values to these tags, but they do not seem to overwrite them |
4/27/2007 5:59 PM | |
Posts: 1275 Rating:
|
Glad to help. Best regards, Danielle |