hello i have one s7 1200
but 1-on hmi i put some touch on-off soft,i connected tag,but when i run plc,not work,practicaly,i need from hmi when i touch the switch,to on-of one output [schnippschnapp]i am in italy,and i talked this week more times with siemens office milano,italy,,they told me ,,i call you back,but nothing,they not respond thanks AttachmentDIGITAL+ANALOG1.zip (905 Downloads) |
||
Last edited by: O_Moderator at: 6/30/2013 8:31 PMsecond question is splitted to /tf/WW/en/Posts/93877#top |
|||
6/29/2013 9:39 PM | |||
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, Please provide snapshots of the button you have problem with.It is normal to define tags in "event" properties of button,But as shown in the attachmnet there is no action defined for selected button.[schnippschnapp] Best regards Hamid Hosseini Attachmentbutton.zip (1112 Downloads) |
||
Last edited by: O_Moderator at: 6/30/2013 8:36 PM |
|||
6/30/2013 9:32 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello AutoGen_667937, There are lots of issues discussed in this thread and even a wrong selected conference.I can only help you about the "button" and a bit in PID issue.For the button issue, please follow what I have done:
Best regards Hamid Hosseini Attachment1200_button.zip (932 Downloads) |
6/30/2013 11:42 AM | |
Posts: 55 Rating:
|
cable lan,plc-switch(tp-link 1gb)-hmi-computer when i go in networking devices,i can see,plc communicate using profinet with hmi,i have connection i can go online,fo test my hw switch PHYSICALand work ,i can on-off all out,Q0..Q4,using I0.0....I0.5, i connected and write event,for modify bit,in hmi,each button on-off, i put bit for on and reset for off when i dont have connection between plc and hmi,from hmi the button,remain on but when i connect with plc,no,work just with phisical switch,i cant understand where is something wrong can you help me? thanks |
6/30/2013 11:53 AM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, In your original project there was no connection defined between the PLC and HMI.Check as attachment.The procedure is simple, just add HMI to same network in "network view" or "device configuration". Best regards Hamid Hosseini AttachmentNETWORK_CONNECTION.zip (984 Downloads) |
Last edited by: hdhosseini at: 6/30/2013 11:54 AMLast edited by: hdhosseini at: 6/30/2013 11:54 AM |
|
6/30/2013 12:11 PM | |
Joined: 1/28/2012 Last visit: 7/23/2024 Posts: 519 Rating:
|
I have little doubt that your PLC is not communicating with HMI. . |
Regards, |
|
6/30/2013 12:26 PM | |
Posts: 55 Rating:
|
and i have some dubt but i connected and plc with hmi directly,with cable ln direct or crossover,nothing changed,so.......
|
6/30/2013 12:53 PM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
Hi, Give your HMI screenshot after configure all the connection as per network connection pdf
|
6/30/2013 1:22 PM | |
Posts: 55 Rating:
|
please wait ,just some min,i reinstaled w7,step 7......new programm plc,hmi |
6/30/2013 3:07 PM | |
Joined: 1/28/2012 Last visit: 7/23/2024 Posts: 519 Rating:
|
Try one thing. . Try sample program. . E.g. 1. Take one IO field, and assign proper PLC tag to IO field. . Transfer program. . If IO field shows ###### instead of Tag Value, then it concludes that your HMI is not communicating with PLC. . 2. Take one circle or rectangle & give apperance animation for memory one bit or any hardwire DI. . Transfer program & check animation. . |
Regards, |
|
6/30/2013 5:57 PM | |
Posts: 55 Rating:
|
can you see this pdf? i try to use swtich designed in hmi,to comand I0.0.....but not work WHAT IS WRONG another problem i used pid compact, now i can see the variable tension in tia v12 trial,and in output,but in hmi the in and out is remained in max AttachmentPLC_1.pdf (848 Downloads) |
6/30/2013 6:03 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, By command on I0.0 you mean to write on input? I am afraid that is not possible.Try memories and outputs. Update:No thing new in the ".pdf" file. Best regards Hamid Hosseini |
Last edited by: hdhosseini at: 6/30/2013 6:10 PM |
|
6/30/2013 6:20 PM | |
Posts: 55 Rating:
|
from computer or electrical panel? |
6/30/2013 6:35 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello again, Inputs are interface of mahine to PLC,Switches transmitters and all othere devies .They can be forced for maintenance job (for example).Outputs are our control over machine actuators. I an say barely we send command from HMI to an actuator such as a pump.We need to process data received from operator via HMI and condition received from I/O.My suggestion copy you commands to memories and then use them in your program. Memories are like inputs and they are packed byte wise.For example M0.0 , MB10 and... . Best regards Hamid Hosseini |
6/30/2013 7:27 PM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
HI, Have got the communication. If yes I am telling you the step to do on one motor from HMI after some time i will program for stop . delete all the network in ob1 after that follow the below steps in network 1-----> from bit logic command use one NO contact after that one output coil like below Network1 --------------| |-------------( ) name the no contact as M100.0 AND THE output coil as Q0.0 In HMI select a button------> in the properties of button----->select the comand setbit----->give the address of M100.0 after successfull compilation check the runtime if you click the button it will set the NO contact and it become NC and output will get on
|
6/30/2013 8:27 PM | |
Posts: 55 Rating:
|
thank you,my friend,with ,M100.0......WORK but i not finished,this is just begining,you know...... now i have one tension source 0-11 v,reglable,which help me for use pid compact and i draw the bar,0-10v for in and out when i have any tension on, in input ,the bar is full,just if i stop plc,change in white=zero in commisioning,work,in out,i misured,is good,but i cant see varied level in graphic,but the bar is always full can you help me,please? thanks
|
Last edited by: AutoGen_667937 at: 6/30/2013 9:31 PM |
|
6/30/2013 9:23 PM | |
Joined: 1/28/2009 Last visit: 8/31/2025 Posts: 6874 Rating:
|
Hello, You should check if converted data from analog input assigned to the Bar.Check scale of bar and at the same time scale of variable assigned to the bar.I guess there is a mismatch. Best regards Hamid Hosseini |
Last edited by: hdhosseini at: 6/30/2013 9:26 PM |
|
6/30/2013 10:03 PM | |
Posts: 55 Rating:
|
i checked again,i can not understand why the in is blocked in full,i give this photos what is wrong
AttachmentFull page photo.pdf (808 Downloads) |