6/27/2013 7:57 AM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating:
|
Dear Sir, While configuring baumuller Servo drive with Siemens PLC on profibus, Drive is online on profibus and showing device status OK but data transfer is not taking place from drive to plc and vice versa. Baumuller engineer is saying that there is mismatch of configuration from PLC side and asking to consult Siemens expert for this. I am attaching the screen shot of hardware configuration with random values obtain in vat table. please provide the solution regarding its configuration for proper data transfer. ThanksAttachmentConfiguration.zip (733 Downloads) |
6/27/2013 9:14 AM | |
Joined: 4/24/2006 Last visit: 9/15/2025 Posts: 9027 Rating:
|
Hello, Are you using SFC14 and SFC15 to communicate with Drive? Best regards, Wizard |
6/28/2013 11:30 AM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
Hi, please give this screenshot (Red mark area) Parameter assignment area
|
6/28/2013 11:41 AM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating:
|
Dear Sir, Please find the screenshot for the paramter required by you. There plc configuration file also. AttachmentConfiguration.zip (493 Downloads) |
6/28/2013 12:25 PM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
Sir, Give the GSD file also
|
6/28/2013 1:26 PM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating:
|
Dear Sir, These value are steady and not changing. As earlier said, Baaumuller engineer is saying that proper configuration from master side is to be done. Tried many times but could not succeed to fetch values. still finding the way to debug it. please find the GSD. AttachmentGSD.zip (462 Downloads) |
6/28/2013 3:20 PM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
Dear Ashishm, I found this error afternoon itself but i stuck up with this cyclic and acyclic data transfer between drive and master ... Hope soon we will solve this problem.... master won't write anything please check the attachment for your reference
AttachmentNew Folder.zip (420 Downloads) |
6/29/2013 11:52 AM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
Hi, please find the attchment.some important points to check???
|
7/7/2013 4:18 PM | |
Joined: 2/1/2011 Last visit: 9/13/2023 Posts: 186 Rating:
|
Dear Sir, Thanks For replying to problem and finally problem is resolved. There was no requirement to change in settings from PLC side. At drive side settings have to be made proper |
This contribution was helpful to
3 thankful Users |
7/10/2013 4:21 AM | |
Posts: 30 Rating:
|
Hi, Your screen showing the communication is up and the initial values have been read out from BAUMULLER drive. but you saing the values are not updated. my investigation is this, from your Area Assignment of I/O, the 1st module you entered is "Non-cyclic data module" , in this case, the processing of the non-cyclic data requests is executed in the PLC with low priority and vales will only be updated upon request. That's the general rule I guess you already knew. and you are not using Non-cyclic area as communication at this case. the area you are concerning are Cyclic Area, which are PID260 and PID264, thats would be the actual value read out from drive., and if you could also attach more screen shots on Input/Output 256~259, also the status/ control word, from that may tellus more about your status.alsotry togglethe control word see how the value looks like. However, I don't think the problem on DP/communction part. Cheers, |
7/10/2013 6:48 AM | |
Joined: 4/17/2012 Last visit: 6/17/2025 Posts: 474 Rating:
|
Dear Ashishm, Good work... Thanks for the update
|
Follow us on