9/16/2018 5:08 PM | |
Posts: 29 Rating:
|
|
9/16/2018 5:08 PM | |
Posts: 29 Rating:
|
|
9/16/2018 5:09 PM | |
Posts: 29 Rating:
|
|
9/16/2018 5:10 PM | |
Posts: 29 Rating:
|
i don´t know if it matters but when i go through V-assistant i can jog the motor without any problems? |
9/17/2018 2:59 AM | |
Joined: 10/7/2009 Last visit: 8/8/2025 Posts: 266 Rating:
|
Dear Simon, |
9/18/2018 7:53 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello, You need support package for TIA portal V14 - HSP0185 V1.0 (refer page 8 of 72341852_STEP7_TIA_Portal_V14_HSP_en.pdf(936,9 KB) & can be downloaded from Support Packages for the hardware catalog in the TIA Portal (HSP) HTH. |
Last edited by: Jen_Moderator at: 9/18/2018 12:10:41 PMOptimized link. |
|
9/18/2018 7:56 AM | |
Joined: 5/12/2006 Last visit: 9/1/2025 Posts: 22686 Rating:
|
Hi, this HSP can be used here because this V90PN can only assigned to a S7-1500. If you use another PLC Type (S7-300/S7-1200) then you must use the GSDML Files.
Christoph |
This contribution was helpful to
2 thankful Users |
9/18/2018 3:33 PM | |
Joined: 10/11/2006 Last visit: 8/29/2025 Posts: 6037 Rating:
|
Hello, the project example https://support.industry.siemens.com/cs/ww/en/view/109743917 run with the available V1.00.02.GSDXM;. https://support.industry.siemens.com/cs/ww/en/view/109737269 Check your communication settings in V90 and S7-1200 and set V90 to S mode with Vassistant. Start configuration of V90 with factory settings, to delete old settings. 4.1.1 Configure PROFINET settings via SINAMICS V-ASSISTANT 3.1 Basics regarding SINAMICS V90 PN version When SINAMICS V90 PN works in the speed control mode (S mode), the following telegrams are supported: Standard telegram 1 Standard telegram 2 Standard telegram 3 Standard telegram 5 Siemens telegram 102 |
With best regards, |
|
Follow us on