6/16/2008 1:17 PM | |
Posts: 510 Rating:
|
A screen shot of the details page of the error would be very helpful in diagnosing your problem. Please post it to the forum. Bill |
6/17/2008 5:22 AM | |
Posts: 5 Rating:
|
Hi Bill, I am attaching the Error in detail file for your refernce. Dipesh AttachmentError_IN_DETAIL.pdf (658 Downloads) |
Last edited by: DIPESH at: 6/17/2008 5:22 AM |
|
6/18/2008 12:15 AM | |
Posts: 2661 Rating:
|
Can you also post the diagnostic buffer and the HW config (after exporting)? Verify the ET200M/DP settings. |
6/18/2008 6:37 AM | |
Posts: 5 Rating:
|
Hi Bill, AttachmentDiagnose.pdf (700 Downloads) |
6/18/2008 6:45 AM | |
Posts: 5 Rating:
|
Hi Bill, Attachmenthw.zip (563 Downloads) |
6/18/2008 6:56 PM | |
Posts: 2661 Rating:
|
Bill: In my opinion the problem has got nothing to do with the PII settings. I checked the diagnostic buffer and the HW config and found nothing untoward. DIPESH: I would recommend opening a service request with Siemens tech support. Your problem may be a known issue and the fix may be as simple as installing the latest HSP. You can try with latest HSP from link below, but I would first report the problem to Siemens tech support. Hardware Support Packages (HSPs - 05/2008) Regards |
6/19/2008 1:16 PM | |
Posts: 2348 Rating:
|
1. From which folder you inserted ET200M? As far as i remember there are few of them (ex. DVPV0 Slaves->ET200M) 2. Did you try GSD file instead metadata? |
6/27/2008 4:48 PM | |
Posts: 12 Rating:
|
Please try with PCS 7 recommended IM's and Modules. Otherwise this error will prompt |
Follow us on