Dear expert, where i got sample project for Hardware redudancy.
|
Rajkiran Patil |
|
11/16/2011 12:06 PM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
HelloRAJKIRAN, Open SIMATIC Manager and open the sample projects instead of user projects. you will find 2 projects, ZXX01_14_HSystem_S7400H for basic hardware configuration. ZXX01_15_HSystem_RED_IO for redundant I/Os configuration and programming. Best regards. H-H
|
This contribution was helpful to
1 thankful Users |
11/30/2011 12:59 PM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
HelloRAJKIRAN, Are you sure you have put your user program between FB450 and FB451? Please upload your diagnostic buffer and definitely it will be better if you upload your sample project here for better investigation. I also recommend to reassign the I/O modules to a process image partition that's updated with a cyclic interrupt and write all your code in this cyclic interrupt. Best regards. H-H |
11/30/2011 4:27 PM | |
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
Dear H-H, Find attached both programm for investigation..... 1.without logic showing me all redudancy 2.with logic not showing DI redudancy( in next post) plz reply what is problem Attachment1_red_nologic.zip (825 Downloads) |
Last edited by: RAJKIRAN at: 11/30/2011 4:28 PMRajkiran Patil |
|
11/30/2011 4:34 PM | |
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
Find attached second programm.... 2.with logic not showing DI redudancy Attachment2_red_withlogic.zip (721 Downloads) |
Rajkiran Patil |
|
11/30/2011 4:44 PM | |
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
find attached dignose file(Dignostic Buffer).
AttachmentDiagnose_Red_Problem.zip (764 Downloads) |
Last edited by: RAJKIRAN at: 2/18/2012 9:56 AMRajkiran Patil |
|
12/1/2011 1:35 PM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
HelloRAJKIRAN In hardware configuration, CPU properties, H parameters then redundant I/O data blocks are 1 & 2. You can't use DB1 and DB2 in your project. You have to change either DB1&DB2 in your program or change the redundant I/O data block in HW configuration. You have assigned your I/O modules to PIP1 which is updated with OB35. So, remove all networks in OB1 except network one (Report System Error). Write you program in OB35 between FB450 and FB451. Also, you don't need to call FB450 and FB451 in OB10. Best regards. H-H
|
This contribution was helpful to
2 thankful Users |
12/1/2011 3:06 PM | |
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
You have assigned your I/O modules to PIP1 which is updated with OB35. So, remove all networks in OB1 except network one (Report System Error). Write you program in OB35 between FB450 and FB451. Also, you don't need to call FB450 and FB451 in OB10. Best regards. H-H
|
Last edited by: RAJKIRAN at: 12/1/2011 4:19 PMThanks Rajkiran Patil |
|
12/1/2011 3:07 PM | |
Joined: 8/18/2009 Last visit: 7/28/2025 Posts: 558 Rating:
|
Dear H-H, From where I can change redundant I/O data block in HW configuration. |
Last edited by: RAJKIRAN at: 12/1/2011 3:08 PMRajkiran Patil |
|
12/1/2011 4:07 PM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
HelloRAJKIRAN
In HW configuration> CPU properties>H parameters. Please see my attachment. Best regards. H-H |