(2)| 9/15/2022 4:32 AM | |
|
Joined: 1/21/2013 Last visit: 12/24/2025 Posts: 4365 Rating:
|
Hi hossamhegab, for selecting the hardware, I would recommend the TIA Selection Tool. This software is free for use and available as cloud version and as standalone version for Windows 10. In both versions, you can use the plant configuration to get a hardware selection for your requirements. Kind regards |
| 9/15/2022 7:31 AM | |
|
Posts: 23 Rating:
|
Already I have tried to use tia selection tool but I don't not the most appropriate cpu and whether using ET200 or not and which model of et200 I will ise |
| 9/15/2022 8:01 AM | |
|
Joined: 1/21/2013 Last visit: 12/24/2025 Posts: 4365 Rating:
|
Hi hossamhegab, the choice of the PLC does not depend on the amount of I/Os. For this, the required performance and the required memory would be important. It might also be important to know, if integrated safety or enhanced technology functions would be required. In the current situation, the delivery time may also be a decisive factor for the choice of hardware. If you think about the use of the decentralized periphery, for in-cabinet use, I would recommend the SIMATIC ET 200SP. For periphery outside the cabinet, the SIMATIC ET 200AL. For further advice, I recommend contacting the Siemens Technical Consulting. You can use the contact database to find the contact details for your location. Kind regards |
This contribution was helpful to
|
|
| 9/24/2022 6:48 PM | |
|
Posts: 23 Rating:
|
Thanks for all, I found this documentation very helpful and now I can select the system easily.
Attachments7-1500_in_a_nutshell.pdf (744 Downloads) |
This contribution was helpful to
|
|