(5)| 5/27/2021 9:53 AM | |
|
Posts: 5521 Rating:
|
hi, can you show us how you called the PID_Compact? Tuning is recommented to find the optimal PID parameters. regards, |
| 9/22/2021 12:01 AM | |
|
Posts: 3 Rating:
|
maybe you just need to "Reset" the block (in the reset Input). I had a similiar problem and everytime the PLC power off, the PID block started disabled. |