Ok, to confirm the higher resolution (more bit) the more accurate the value will be since the PIW range will be larger? |
| 6/24/2024 6:10 AM | |
|
Joined: 7/9/2015 Last visit: 12/17/2025 Posts: 4493 Rating:
|
Hi, no, the PIW range is the same but the values between 0 and 27648 inc have a higher accuracy. This is what I wanted to tell you in my last post... Also check this FAQ for understanding: Entry type:FAQEntry ID:39334504,Entry date:04/01/2016(114) Rate For an S7-1200/S7-1500 controller in STEP 7 (TIA Portal), how do you scale integer values in real numbers and vice versa for analog inputs and outputs?Regards, Towome |
|
|
|