Hello Brad27243, Please note the measurement range limits for wire break detection, they must be 1...5 V or 4...20 mA. With the rest the function is not available: Parameter description analog input By default TIA Portal configures the 2-wire as 4...20 mA but the 4-wire as -20...+20 mA |