Hello, In My case it is TP700 previously it was in TIA v15.1 and i upgraded it to TIA v16, after downloading HMI it is showing the error "The configuration file "Flash\Simatic\pdata.fwc Could not be loaded. application is terminated.
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/06/2022 12:08:13New subject after splitting |
|
This contribution was helpful to
1 thankful Users |
10/11/2022 12:56 PM | |
Joined: 8/3/2009 Last visit: 9/9/2025 Posts: 16368 Rating:
|
Hello Nikhil I4.0 Check in your TIA HMI Projct your project if you have updated the Image Version of the HMI to V16. Load also a dummy project, does this work? Try to delete the temporary data with LINK then load again If nothing helps do a Reset to Factory Settings LINK Bye Murof |
If this Information really helps, you could use the Rate function |
|
11/27/2024 5:14 PM | |
Joined: 8/9/2016 Last visit: 5/28/2025 Posts: 1 Rating:
|
I forced the same problem and my first search result was this post. Problem is a wrong operation system for the runtime you want to start. You can't run a V18 runtime with v17 image installed. In my case it was TIA V17 with17.0.0 OS installed, but run into the same problem. I updated to the latest OS version available. Downloaded Project to the panel and it was ok.