Hi, Is the textual name existing in the symbol table? Otherwise the system does not recognize the connection and mapping could not be completed. |
If I could help you, you can use the RATE button. Thank you. |
|
2/18/2025 6:38 PM | |
Joined: 2/1/2010 Last visit: 9/5/2025 Posts: 212 Rating:
|
I can reproduce your results exactly. There is definitely something going on which is different from how the behavior used to work. Most likely there is a bug happening. You can also get interesting results when using Technological List Editor to assign signals instead. They are enterable there, but you will get errors/warnings about software being not installed, but once you acknowledge it, the assignment takes. If you use the right click signal assignment in POV it works, but who wants to do that, the whole point of POV is bulk engineering and right click is certainly not bulk. My suggestion: (many of us should) file SIOS tickets and use Technological Editor for bulk signal assignment instead of POV until Siemens can patch whichever subsystem is causing the issue. (probably TH and/or IEAPO is my guess) Hopefully they can fix this soon as more and more people are ready to deploy on v10 from scratch instead of upgrades. |