Hello ahmed_2001 No it is not possible, OPC DA (DCOM) is not supported directly by the controller. for OPC DA (DCOM) you need a windows system. so you would need a OPC DA Server on Windows that communicates to the S7 via S7 protocol like the Simatic Net OPC Server: https://support.industry.siemens.com/cs/de/en/view/109474300 On the Controller directly only OPC UA Server is supported. Bye Murof |
|