Has anyone managed to get a new 1514SP to work with a old TP900 comfort panel? I am using TIA V20 and cannot get the connection running. I have followed the following doc to the tee but still nothing: No connection to PLC after WinCC Panel Images V17 Update 6 - ID: 109820712 - Industry Support Siemens
|
| 5/16/2025 10:20 AM | |
|
Joined: 4/24/2006 Last visit: 12/24/2025 Posts: 9097 Rating:
|
Hello, Perhaps this link might help: Configuration of an HMI connection to S7-1500/S7-1200 CPUs Best regards, Wizard |
This contribution was helpful to
|
|
| 5/16/2025 11:21 AM | |
|
Joined: 10/12/2015 Last visit: 10/23/2025 Posts: 19 Rating:
|
Thank you sir, that config did the trick. |