Hello; Maybe you should consider upgrading the firmware of your "spare" CPU so it maches the frimware of the CPU yoi need to replace? https://support.industry.siemens.com/cs/ca/en/view/109474703 Hope this helps, Daniel Chartier |
This contribution was helpful to
|
|
| 8/17/2025 2:50 PM | |
|
Joined: 8/15/2025 Last visit: 11/21/2025 Posts: 13 Rating:
|
Thanks Daniel Chartier, I have found the “Download Operating System Updates V4.5H CPU412-3H / CPU414-4H / CPU414-4H PG / CPU417-4H ” and will follow the procedure for upgrading firmware from 5.2 to 5.6 step by step.. not able to do from 5.2 to 5.6 I understand. https://support.industry.siemens.com/cs/de/en/view/109474703 I have received two file for the Diagnostic buffer of module CPU 417-4 H for both Rack 0 and Rack1 in txt format. Will go to Classic forum to attach for review and advice. I am listing the errors that have occurred since the 11th August 2025 to 16th August 2025 for now to gain a better understanding of what the sequence of event are. The history of issues however started way back in 2023.. lol |
Last edited by: Moderator_Lan at: 08/18/2025 07:59:52link optimized Colin Canham |
|
| 8/17/2025 2:52 PM | |
|
Joined: 8/15/2025 Last visit: 11/21/2025 Posts: 13 Rating:
|
AttachmentPGS_A.txt (205 Downloads) |
Last edited by: AutoGen_7010283 at: 08/17/2025 14:54:49Colin Canham |
|
| 8/17/2025 2:57 PM | |
|
Joined: 8/15/2025 Last visit: 11/21/2025 Posts: 13 Rating:
|
PGS_A.txt is the Diagnostic buffer of module CPU 417-4 H for Rack 0 the next attached PGS_B.txt is for the Diagnostic buffer of module CPU 417-4 H for Rack 1
AttachmentPGS_B.txt (188 Downloads) |
|
Colin Canham |
|
| 10/7/2025 6:41 AM | |
|
Joined: 8/15/2025 Last visit: 11/21/2025 Posts: 13 Rating:
|
1. I investigated loss of connection to Profibus slaves for your comment, "Next, your diagnostic buffer shows a large amount of OB122 errors in FC 1070 and higher. This often happens when you lose connection to a Profibus slave or Profinet IO Device and attempt to read or write values while they are not accessible." I have only assessed events that occurred on the 11th August 2025 concerning Profibus slave communication “failure” and “return” these are listed sequentially below as taken from the PGS_A.txt file provided. From the event 2175 through event 2152 there are fourteen events listing the “Distributed I/Os station Failure”. Profibus slave nodes 11, 12, 13, 14, 15, 16 , 17, 4, 5, 6, 7, 8, 9 & 10. Event 2175 of 3000: Event ID 16# 39C4 Event 2174 of 3000: Event ID 16# 39C4 Event 2173 of 3000: Event ID 16# 39C4
From event 1368 through event 1025 there are fourteen events listing the “Distributed I/Os station return”. Profibus slave nodes 13, 14, 15, 16, 17, 4 , 5, 6, 7, 8, 9, 10, 11 & 12. When following the events 2178 to 2176 below, I understand that the loss of redundancy, due to Standby CPU failure of the affected CPU in Rack 1, is the initial step, leading to the Stop of event 2176. Event 2178 of 3000: Event ID 16# 7301
Event 2177 has the Master CPU in Rack 0 change from redundant mode to solo mode and is in Run operating mode already, being the Master CPU of the pair of CPU's. Event 2177 of 3000: Event ID 16# 43E3
Event 2176 is the strange situation where the Master CPU of Rack 0 in Run mode goes into Stop mode because it's partner CPU of Rack 1 "is also a Master... (link-up error). Surely if event 2178 has the "Standby" CPU failure of Rack 1 at 10:08:59.297 PM 08/11/2025, it can't suddenly become a master at 10:08:59.775 PM 08/11/2025, 478ms later... Event 2176 of 3000: Event ID 16# 43D4 3. Also noted below, a Standby CPU submodule error in Rack1. Event 2188 of 3000: Event ID 16# 45E4
|
Last edited by: AutoGen_7010283 at: 10/08/2025 06:07:28Re-arranged layout of information for better clarrity of points being noted. Colin Canham |
|