(2)| 8/25/2025 12:04 PM | |
|
Joined: 1/2/2012 Last visit: 12/30/2025 Posts: 32 Rating:
|
Hi Chris, I saw this article on the support site:Desigo PX controllers: No alarm notification to stationary alarm receivers using ... - ID: 109990747 - Industry Support Siemens This could be your problem if you have the latest FW version of the PXC controller. They recommend a downgrade in this article. ================================================================= RecommendationDue to the above facts, we recommend for the time being not to install from the XWP_Firmware-Library_V6.30.495 the FW_PX..._V6.00.345 or FW_PX..._V6.30.037 on any PX devices. Note: For Desigo PX sites where the specified affected firmware is already installed, we strongly recommend downgrading to the previous firmware:
======================================================================== Best regards, Fons |
Last edited by: Moderator_Lan at: 08/25/2025 13:41:28link optimized |
|
This contribution was helpful to
|
|
| 8/26/2025 5:40 AM | |
|
Joined: 10/12/2023 Last visit: 12/18/2025 Posts: 147 Rating:
|
Hello Fons, We have X.338 FW on all PXCs, but thanks for the helpful article. |
|
Best regards, |
|
| 10/3/2025 7:17 AM | |
|
Joined: 5/16/2016 Last visit: 12/19/2025 Posts: 92 Rating:
|