12/8/2009 3:07 PM | |
Joined: 3/29/2006 Last visit: 5/29/2017 Posts: 151 Rating:
|
You can download the parameters from the V3.3-card into the V3.2 one. The parameters in the "fault"-list at the end of download must be checked by hand. Whether you can use the V3.2x depends from the x (parameter r828.01). "3" ==> V3.23 would be o.k. But you can upgrade the V3.2x to V3.33; see http://support.automation.siemens.com/WW/view/en/25203927 This is the firmware only for compact-/chassis- units, NOT for compact plus (VC+). You will find other versions, too. For parameterizing a new drive usingan upread-file from another drive, you should always use a file of "Basic device, changes only"; compared to factory settings. Firmware-upgrade from V3.x to V3.y will result in factory-settings of the drive !! You need a DriveMonitor-cable with a small switch / jumper between pins 1-5-9 and 4 on drives-side. This will set the drive into boot-mode, if the plug is fixed on drives-side and the 24V will be switched on; mentioned in the readme included in firmware-download-zip-file. |