Hello everybody! Anibody have sucess in connection between S7-315 2-PN/DP and Danfoss VLT302 via MCA120 Profinet card? I am try to use this solution, but have a message warning W34 and not see any value on status/control word display! Anibody have any ideia about this? Thanks for any help Splitted from Profinet Communication through a danfoss drive.
|
Last edited by: O_Moderator at: 6/22/2011 12:26 PMnew subject after splitting |
|
6/22/2011 11:34 AM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Dear NewTech, Please check the IP address and Device Name (host name). Have a look at this link: http://mcliterature.danfoss.com/WebPublish/doc_MG90U202.pdf Best regards, Wizard |
10/28/2011 11:34 AM | |
Posts: 2 Rating:
|
I have the same problem with connection. NewTech, how did you solve the problem? |
11/1/2011 12:06 AM | |
Joined: 2/23/2007 Last visit: 2/19/2023 Posts: 75 Rating:
|
I solved this problem by reversing the control and status words... and direct write status by danfoss manual..AttachmentCreate UDT.pdf (670 Downloads) |