(0)| 1/15/2012 5:37 PM | |
|
Posts: 7 Rating:
|
Hi, Im trying to connect a PTC to Sinamic G110 inverter. I saw this tutorial:https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&objid=42470166&caller=view But i have a little doubts: I want theinverter stops motorwhen the temperatureis100degrees. How do I knowthe value of thePTC touse?Is there anycalculationto do?And about 1K resistor? "Toenablethe tripfunction setup oneof thedigitalinputsusingDIN0(P0701)orDIN1(P0702)orDIN2(P0703)to avalueof29 (externalfault)."ImusingtheDIN1P0702=29. How the inverterdetects the increase oftemperature by theexternal fault? I need your help guys. I only have 5 days to finish the projet for school :/ Best Regards
|
| 1/16/2012 4:36 PM | |
|
Posts: 7 Rating:
|
SO, how I Know the PTC to use? |
| 1/17/2012 10:12 AM | |
|
Posts: 739 Rating:
|
pls see operating instruction chapter 3.4.6 External Motor Thermal Overload Protection http://support.automation.siemens.com/WW/view/en/22102965 |