1/21/2013 8:00 AM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
Hello. Yes, it is possible via binary input or via PLC control word. To use binary input for acknowledge the fault look at function diagram sheet G180 ofthemanual, set P648=9 (bit-serial input of control bits) and set e.g. P665=B010 (terminal 36).
|
1/21/2013 9:44 AM | |
Posts: 42 Rating:
|
Thank you |
1/21/2013 11:46 AM | |
Posts: 42 Rating:
|
Hi, Thank you very much. It is working |
Follow us on