can we use 3ru1146-4jb1 for dc motor 440vdc/48amp ? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 9/13/2015 3:37:12 PMNew subject after splitting |
|
| 4/25/2016 8:36 AM | |
|
Joined: 3/17/2013 Last visit: 4/28/2025 Posts: 481 Rating:
|
Not sure for DC voltages, Data sheet mentioned for AC3 only even though current wise 48 A comes in the range Vijay Attachment3RU1146-4JB1.pdf (1529 Downloads) |
| 4/25/2016 9:13 AM | |
|
Posts: 8092 Rating:
|
Yes but remember to connect all 3 poles in series. Please refer the attached extracts from SIRUS system manual for LV switch gear. |