(2)| 12/15/2008 4:16 PM | |
|
Posts: 9 Rating:
|
Hi there, is there a way I can copy timers values (On or OFF) so that when I change the value on timer A the value in timers B and C.. change? Please advice |
| 12/16/2008 12:24 PM | |
|
Posts: 9 Rating:
|
Hi there, What I need to do is change the on delay times of all the timers when I change one. Please see attached. I need the time delay of timers 2 and 3 to change automatically when I change timer 1 Attachmenttimers.pdf (1032 Downloads) |
| 12/18/2008 12:38 PM | |
|
Posts: 661 Rating:
|
Hi course you can. Please look at the example "Using the reference function": http://www.automation.siemens.com/logo/html_76/products/02Applications/index.html (example on page 4). You need a LOGO! 0BA5 or 0BA6. The setpoint for the timers (on-time)you enter in V1 of the analog MUX. Then you refer the on time of alll timers to the MUX. V1 of the MUX you can display in a messagfe text. So it´s very easy to adjust thevalue quickly. AttachmentSetpoint via MUX.zip (889 Downloads) |