(2)| 2/24/2021 6:49 AM | |
|
Posts: 8092 Rating:
|
Hello, You need to use SMC 30 module to connect motor encoder connection & via Drive CLiQ SMC30 can be interface to CU250S. Please refer attached sheet for M23 HTL encoder pin connection details. Please refer manual https://support.industry.siemens.com/cs/de/en/view/109754294 chapter 8.6 for SMC 30 details. |
| 2/24/2021 7:35 AM | |
|
Posts: 31 Rating:
|
Thank you for sharing. |
This contribution was helpful to
|
|
| 2/25/2021 3:28 AM | |
|
Posts: 31 Rating:
|
Hi, Instead of using SMC 30 module, can I connect the motor encoder directly to the X2100 Encoder Interface on the CU250S-2PN? |
| 2/26/2021 6:06 AM | |
|
Posts: 8092 Rating:
|
Yes you can connect. Please check the pin configuration at encoder end & at CU end & connect the connections correctly. HTH |
Follow us on