5/23/2014 10:43 PM | |
Posts: 38 Rating:
|
Hello Experts, One of our 6RA70 drives give A031 alarm near base speed, i have check P590 & P591 Its correctly set Speed set and actual, P388 = 3 % P390 = 3 SEC , FOR same drive i have attached trace file where we can easly see that when speed setpoint increase that time field also get weaken and arm current also increas but speed not match, because of same we are getting product defect. pls give suggetion, what can be done to resolve same. Thanks in advance
Attachment6ra70 A31.zip (419 Downloads) |
5/24/2014 12:40 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello Meet What is your application ? Do you have a Current Limit / Torque Limit Active ? If there is a Current limit active and Drive is operating a current limit, then you will get this alarm. This is quite normal in Winder applications where speed setpoint is always higher than the web speed with a Torque limit applied. In such cases the Threshold of the alarm needs to be increased. Even in non Winder applications ( Extruders , Mills etc ) , if the Drive reaches its Current Limit / Torque limit ( Fixed limit in Drive parameters / variable limit through Analog Input / Profibus ) , you can have this alarm. In such cases, you can either increase the limit ( if possible ) or reduce the load. Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
1 thankful Users |
5/24/2014 2:48 PM | |
Posts: 38 Rating:
|
Hello navang thank for support, my application is rolling mill, I have check all para related to limiting P171 = 70% P172 = -70% P181 = 300% P182 =-300% P510 & P511 = K2 FIX 200 P603 = K1 FIX 100 P604 = K9 Block specific. [ is there any more limit para i need to check ? or this is it ] here what i can see my minimum Limit is 70% where as if you see in Trace file current was only 30% when speed not match. i think from above parameter i can't see limit from profibus or else, although i have attached drive monitor file also pls refer and guide what else can be the prob. Thanks in advance for your kind support.
Attachment6ra70 A31 dnl.zip (383 Downloads) |
5/24/2014 8:21 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello Meet KSNis right 70% Current Limit is low for Rolling Mill Application. Usually Rolling mill duty have Current limit setting at 100 % or more .
Has there been any change in your Mill or in Rolling parameters ? e.g. is there any change in Material Hardness, Thickness , Screwdown load , Mill Reduction, Increase in Line Speedetc, which could cause the Motor current to reach current limit. You really need to monitor the motor current at the time of Alarm .. as that is most likely to be the problem. Have any Drive parameters been changed recently ? In Particular I am preplexed by your setting of Speed Dependent Current Limiting ( P104to P 108 ) As per your Drive Configuration, the Rated Motor Speed in 500 RPM, while in Speed Dependent Current Limiting, the Current is being limited to 0.1Amp at 250 RPM Was the Drive working earlier at same line speed ?? Hope this helps Cheers Navnag |
Last edited by: Navnag at: 5/24/2014 8:22 PMThere is no such thing as the last bug in a program |
|
5/25/2014 2:02 PM | |
Posts: 38 Rating:
|
Hello KSN, ok I will check all para at next Alarm.
|
6/20/2014 11:00 AM | |
Posts: 38 Rating:
|
Hello Experts, once again A-31 appear in one drive, here i have attached its Trace file, yes in trace it is showing current limit reach, in limit word r40-bit 11 operated current limit, but as i have check here actual current is not reached 100%, as per para setting P171 & P172 = 100%, but i dont know how this K-131 is less then 80%, pls guide me how this K-131 value came 80 %. and general i have observed in my plant drives Limit word bit-2, 9, 10, 11 is commonly getting high, how to resolve same. Thanks in advace for your support.
AttachmentA0-31 Alarm Trace.zip (401 Downloads) |
6/24/2014 3:25 PM | |
Posts: 38 Rating:
|
Hello Experts, once again A031 alarm came in our drives, and here i have attached its trace file as requested parameter, Pls guide me what can be done to resolve this, in this trace i have observed that here Current and firing angle both going in limit, 1) up to which extent current limit can be opened ? here required or not ? 2) Minimum Firing angle is ok here or max at which limit it can be set ? 3) what other reason for this limitation ? all other your suggetion and guidance are accepted. and one more query, pls look at K131 jpg photo, here you can see All limit para set greater than 100%, still K131 is showing only 65% how ?
AttachmentA031 Trace.zip (352 Downloads) |
6/25/2014 9:13 PM | |
Posts: 38 Rating:
|
in one 575volt drive (motor 600volt), P78 is set to 550 and in its trace it has 100% line voltage continues, still whenever A031 alarm come in that drive, its Actual current get reduced, this is also unable to understand- can you give some idea about this. Attachmenta31 curr reduce.zip (357 Downloads) |
Last edited by: Meet at: 7/5/2014 8:58 PMHello Experts, pls give some suggestion, why in attached trace file application, whenever A31 alarm come, why its current get reduce ? (here my observation is A31 alarm comes because of current limit then current should stay constant right ? ) |
|
5/9/2017 5:02 PM | |
Joined: 3/2/2007 Last visit: 9/9/2025 Posts: 990 Rating:
|
kindly, how did you solve this problem? thank you |