12/27/2012 3:42 PM | |
Joined: 8/25/2006 Last visit: 9/15/2025 Posts: 2218 Rating:
|
Hello. Look here:
|
This contribution was helpful to
1 thankful Users |
12/28/2012 10:41 AM | |
Joined: 10/28/2010 Last visit: 6/3/2024 Posts: 46 Rating:
|
dear sir. DG Rating is 380kva, dg is in good working condition, supply is balance 440AC supply
|
12/28/2012 10:42 AM | |
Joined: 10/28/2010 Last visit: 6/3/2024 Posts: 46 Rating:
|
F030 fault value in r047 is 3 please guide me |
12/29/2012 5:26 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello Eshwar, I understand your query. Again please refer my earlier post, where I have tried to explain you the probable causes of F030 with fault value 3. For more details please see the attached sheet. Moreover when the drive is tripping, during accleration, deaccleration, or during running. Observe this. Best way, if you have oscilloscope, please monitor input AC supply conditions. This will help you to understand the quality of power supply on DG set. AttachmentF030 fault value 3.pdf (380 Downloads) |
Last edited by: PISCEAN 2010 at: 12/29/2012 5:31 AMsheet attached |
|
1/2/2013 6:45 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
|
Hello Eshwar, Please see the manual. Please read chapter no 8 &9 to understand the logic. Hope this helps you. |
2/1/2013 4:16 AM | |
Joined: 10/31/2012 Last visit: 9/8/2025 Posts: 15 Rating:
|
You can find out in parameter U580 also. Usually generator power source is weaker than grid.
Attachment6RA70 commutation failure.pdf (313 Downloads) |
Last edited by: Zaw Zaw at: 2/7/2013 3:55 AMMore info |
|